We are designing exterior steel stud walls for a military hospital.
The lateral resistant system of the 5-story building is special steel moment frame. The floor and roof are light weight concrete on metal deck (diaphgram). The building is under Category IV, seismic design category D, and some parts of exterior wall are subjected to blast load.
I have some questions about the anchor of steel studs to the concrete floor and the under side of metal deck (into concrete through metal deck).
1. Are we expecting concrete floor to crack?
2. Do we need to use those anchors approved for cracked concrete?
3. if we use approved anchors (for cracked concrete), Do we need to use reduced capacity of anchors in cracked conrete? Due to the blast load, the demand of anchor capacity is unreasonably high.
Actually, A/E has approved the shop drawings. we did use approved anchors for cracked concrete. But we did not use the reduced value of anchor in cracked concrete for blast load (the worse case controls the design).
The wall contractor brought up this issue. Any suggestions? if somebody finds that later, it will be big trouble for them.
The lateral resistant system of the 5-story building is special steel moment frame. The floor and roof are light weight concrete on metal deck (diaphgram). The building is under Category IV, seismic design category D, and some parts of exterior wall are subjected to blast load.
I have some questions about the anchor of steel studs to the concrete floor and the under side of metal deck (into concrete through metal deck).
1. Are we expecting concrete floor to crack?
2. Do we need to use those anchors approved for cracked concrete?
3. if we use approved anchors (for cracked concrete), Do we need to use reduced capacity of anchors in cracked conrete? Due to the blast load, the demand of anchor capacity is unreasonably high.
Actually, A/E has approved the shop drawings. we did use approved anchors for cracked concrete. But we did not use the reduced value of anchor in cracked concrete for blast load (the worse case controls the design).
The wall contractor brought up this issue. Any suggestions? if somebody finds that later, it will be big trouble for them.