While creating an automated spreadsheet to perform sub-cooled PSV sizing,I noticed that per API 520, equation D.9 can be used for all cases highlighted in section D.2.2 (multi-component systems with nominal boiling range less than 150°F or single-component systems far from the critical point, and for multi-component systems with nominal boiling range greater than 150°F or single-component systems near the thermodynamic critical point). Therefore, I selected to use equation D.9 in my sheet due to its flexibility.
However, when I try to replicate the propane example from this section using equation D.9 I get a very different omega_s than the one API 520 obtained using equation D.8 (omega_s = 8.515). I am assuming I might be making a mistake while estimating the rho_9 (density evaluated at 90% of the saturation (vapor) pressure corresponding to the PSV inlet temperature (60F).
So, I am using chemcad to do an isentropic flash. My feed stream is at 60F and 300.7 psi (set pressure of 260psig + 10% overpressure +14.7 psi to get to psia). My flash in then isentropic at 96.8 psia, which is 90% of saturation pressure for propane at 60F. As a result of the flash I am getting a density of 31.38, which gives me an omega_s of ~0.15, so not even close to the 8.515 shown in API 520. Am I making a mistake with my flash?