Good afternoon,
I am currently inspecting an existing storage tank ---- nozzles, reinforcement [or lack of]. I am trying to determine whether the client can receive credit for reinforcement, based on their nozzle neck thickness / distance from the shell. The client has ZERO previous history, information and/or any kind of drawings.
Can I get another opinion on the following 650 code literature to better understand how i can address and assess there not being a repad on nozzle greater than 3".
e) The material in the nozzle neck. The strength of the material in the nozzle neck used for reinforcement should
preferably be the same as the strength of the tank shell, but lower strength material is permissible as
reinforcement as long as the neck material has minimum specified yield and tensile strengths not less than 70 %
and 80 %, respectively, of the shell-plate minimum specified yield and tensile strengths. When the material
strength is greater than or equal to the 70 % and 80 % minimum values, the area in the neck available for
reinforcement shall be reduced by the ratio of the allowable stress in the neck, using the governing stress factors,
to the allowable stress in the attached shell plate. No credit may be taken for the additional strength of any
reinforcing material that has a higher allowable stress than that of the shell plate. Neck material that has a yield or
tensile strength less than the 70 % or 80 % minimum values may be used, provided that no neck area is
considered as effective reinforcement.
5.7.2.4 The following portions of the neck of a fitting may be considered part of the area of reinforcement, except
where prohibited by 5.7.2.3, Item e:
a) The portion extending outward from the outside surface of the tank shell plate to a distance equal to four times the
neck-wall thickness or, if the neck-wall thickness is reduced within this distance, to the point of transition.
Thank you!
I am currently inspecting an existing storage tank ---- nozzles, reinforcement [or lack of]. I am trying to determine whether the client can receive credit for reinforcement, based on their nozzle neck thickness / distance from the shell. The client has ZERO previous history, information and/or any kind of drawings.
Can I get another opinion on the following 650 code literature to better understand how i can address and assess there not being a repad on nozzle greater than 3".
e) The material in the nozzle neck. The strength of the material in the nozzle neck used for reinforcement should
preferably be the same as the strength of the tank shell, but lower strength material is permissible as
reinforcement as long as the neck material has minimum specified yield and tensile strengths not less than 70 %
and 80 %, respectively, of the shell-plate minimum specified yield and tensile strengths. When the material
strength is greater than or equal to the 70 % and 80 % minimum values, the area in the neck available for
reinforcement shall be reduced by the ratio of the allowable stress in the neck, using the governing stress factors,
to the allowable stress in the attached shell plate. No credit may be taken for the additional strength of any
reinforcing material that has a higher allowable stress than that of the shell plate. Neck material that has a yield or
tensile strength less than the 70 % or 80 % minimum values may be used, provided that no neck area is
considered as effective reinforcement.
5.7.2.4 The following portions of the neck of a fitting may be considered part of the area of reinforcement, except
where prohibited by 5.7.2.3, Item e:
a) The portion extending outward from the outside surface of the tank shell plate to a distance equal to four times the
neck-wall thickness or, if the neck-wall thickness is reduced within this distance, to the point of transition.
Thank you!