I'm considering installing arc flash detection equipment to trip upstream breakers instantaneously in the case of an arc flash event. My question is whether this equipment can be of any use in instances where the arcing fault current is already expected to be high enough to trip the breaker on instantaneous.
For example, I've got a 1000A breaker which will trip on intantaneous at 10kA or less, and the calculated arcing fault current is 15kA. Will the arc flash detection trip the breaker sooner due to the time it takes for the fault current to build up? Or will the system be completely useless for all types of faults in this case?
For example, I've got a 1000A breaker which will trip on intantaneous at 10kA or less, and the calculated arcing fault current is 15kA. Will the arc flash detection trip the breaker sooner due to the time it takes for the fault current to build up? Or will the system be completely useless for all types of faults in this case?