I further got s situation in one of the projects wherein the existing area classification of a certain area our company is working on has it's extents based from PLANT BATTERY LIMITS. The project calls for an electrical cabinet to be mounted near a piperack. However, this particular area classification drawings indicates the entire piperack to be Class I Div 2 and extending approximately 5ft from the piperack edge in both sides. The area classification drawing is not scaled. We figured out the 5ft extent from the piperack edge based from a civil drawing since it exactly matches the process battery limits.
My concern is that the cabinet length is big that a small portion of it crosses Class I Div 2 if I were to based it from this area classification drawing. There are no pumps on that part and closed piping systems are running above it. There is a liquid hydrocarbon pipe running at an El+14'B.O.P. and at 8.12ft away horizontally but its a closed piping with no valves. I will double check and locate for any drains and whether this drains are normally closed and only being opened during a shutdown (in whioch case should not be considered a point of release).
If that part where my cabinet is located do not have any items substantially near to it as a potential release of ignitable elements, is this going to be a technically justified approach instead of using the Battery Limit based area classification which I feel is over-exagerated?
I was on the belief that area classication extent boundaries should be based from actual sources of release from equipment around our cabinet and do not have to be based from process battery limits. BTW, our cabinet dimension is 8'WD x 7'HT x 1-1/2'DP.
Your views and inputs are highly appreciated.
GO PLACIDLY, AMIDST THE NOISE AND HASTE-Desiderata
My concern is that the cabinet length is big that a small portion of it crosses Class I Div 2 if I were to based it from this area classification drawing. There are no pumps on that part and closed piping systems are running above it. There is a liquid hydrocarbon pipe running at an El+14'B.O.P. and at 8.12ft away horizontally but its a closed piping with no valves. I will double check and locate for any drains and whether this drains are normally closed and only being opened during a shutdown (in whioch case should not be considered a point of release).
If that part where my cabinet is located do not have any items substantially near to it as a potential release of ignitable elements, is this going to be a technically justified approach instead of using the Battery Limit based area classification which I feel is over-exagerated?
I was on the belief that area classication extent boundaries should be based from actual sources of release from equipment around our cabinet and do not have to be based from process battery limits. BTW, our cabinet dimension is 8'WD x 7'HT x 1-1/2'DP.
Your views and inputs are highly appreciated.