Rapt
Thank you for the link to Amdt 2
Apologies as I know this is out of your area but,
I have a question on the alteration to Clause 11.7.5 and want to check if my interpretation is correct
Paragraph 1 is unchanged:-
(Hence where tension exists under any eq loadcase, Ast dowel>Ast wall)
New Paragraph 2 says ignore para 1 if there is no net tension under eq.
New Paragraph 3 says that where wind or some other requirement (presumably that doesn't have a cyclic load requirement (Para 1 sets Astdowel >Astwall for tension under any earthquake case) Ast dowel>0.5*Ast Wall
(I assume that the intent of para 3 is that these bars don't need to be fully anchored as stated in Paragraph 1)
New paragraph 4 says dowel reinforcement shall exceed Cl 11.7.1 as a minimum even where the surface is in compression (I assume that these bars don't need to be fully anchored)
Is it intended that para 4 applies to a tilt up warehouse commercial retail single storey building where we are typically using 1 or 2 dowels at each end of the panel.
This would seem to be extreme?
Cheers