Hi All,
I am currently designing a multi-story residential building with a precast core box acting as the main lateral stability element with a ductility of u=2. Looking at Clause 14.6.7 in AS3600-2018, vertical and horizontal reinforcement must be provided in both faces of the wall and must be split equally:
Lateral stability precast walls are typically provided with central dowels with lapped tension bars to transfer the tension forces in the wall to the foundation. Does the new clause require dowels to be provided on each face, regardless of if vertical panel reinforcement is provided on each face within the wall? Do the tension lap bars/dowels also contribute to the minimum vertical reinforcement requirement in Clause 14.6.7 even if they are provided central?
Thanks for your help in advance
I am currently designing a multi-story residential building with a precast core box acting as the main lateral stability element with a ductility of u=2. Looking at Clause 14.6.7 in AS3600-2018, vertical and horizontal reinforcement must be provided in both faces of the wall and must be split equally:
Lateral stability precast walls are typically provided with central dowels with lapped tension bars to transfer the tension forces in the wall to the foundation. Does the new clause require dowels to be provided on each face, regardless of if vertical panel reinforcement is provided on each face within the wall? Do the tension lap bars/dowels also contribute to the minimum vertical reinforcement requirement in Clause 14.6.7 even if they are provided central?