AS3600 - 2019 2nd Draft For Public Comment
rapt
AU
This should be available for download from Australian Standards mid next week. Nominally Tuesday, but who knows!
Does the public get to comment on the commentaries? Figure C8.1.10.6 has more than its fair share of errors in the 2014 commentary.
Steveh49
It went out to public review before it was printed.
Doesn't look to good does it.
Make up a list of the errors you can spot (I have seen about 4 in a quick look now). Let me know and I will pass it on for inclusion in the next draft.
I'll be honest: I missed the publication of the commentary by about two years. In fairness to myself though, after 4 years I'd given up looking out for it. Are you able to say why it took so long? I'd have thought it would practically be written when the standard itself is released, since any changes have been thoroughly researched and have a sound, explainable basis.
The only error that's not cosmetic is that the requirement of clause 8.1.10.6(c) is ignored. The more than one-quarter of the positive moment reinforcement is shown terminating at a point near the simple support instead of being spread over 2D. I presume the same happening at the continuous support is OK given it's on the compression face at that point but the wording of the standard isn't 100% clear to me.
Otherwise: Positive reinf referred to as negative; negative reinf has a gap but should be continuous across whole span.
Noticed the cosmetic ones. Does not say a lot for the editors and stylists.
Re 8.1.10.6(c), Agreed it does not comply, but I think the justification would be that 25% could have been terminated much earlier, but no sensible engineer would terminate multiple times so the 1st 25% termination point has been extended to be at the same location as the second where a total of 50% has been terminated. This clause is a deemed to comply requirement for the for reinforcement termination based on the real clause 10.4 which also has the 25% termination rule, but it is based on terminating at the point where the reinforcement is no longer required by calculation of strength and development requirements rather than a deemed to comply requirement.
I also do not like end support being shown as a masonry wall and no development of top reinforcement as the deemed to comply case. Most beams would terminate at a column and require proper top reinforcement detailing.
Cannot comment on reasons for the release delay. Most people in the industry know what went on!
FYI folks,
I just checked where you submit comments on the Standards Australia website and code committee has now filled in the responses; accepted, rejected etc to any comments you may have submitted. I found they were quite receptive to the comments raised which is great to see.
Matt,
Could you please copy/paste them here? Or post a screenshot?
I can't seem to access the page you're talking about. Cheers.
Apparently the new code is being released on Friday 29/6!