Hi.
Just wanted to get some views on a basic suspended reinforced concrete deck that has a high degree of restraint.
I have designed the flexure reo to As3600 for service stresses. Then I checked checked this same amount of reo assuming my structure has a high degree of restraint (ie using 0.6% reo for high degree of restraint).
In summary the quantity of reo I have for flexure by itself is more than enough to handle the high degree of restraint for when shrinkage occurs.
The question is, should shrinkage reo be additive to the flexure reo? I was always led to believe that if you satisfy shrinkage with your flexure reo..."you're fine"... But I have my doubts.
Surely the mere action of shrinkage and the stiff columns means that tension builds up in the slab (ie so now we have the original flexure moment now with tension included). Does this exaserbate service cracking?
Just wanted to get some views on a basic suspended reinforced concrete deck that has a high degree of restraint.
I have designed the flexure reo to As3600 for service stresses. Then I checked checked this same amount of reo assuming my structure has a high degree of restraint (ie using 0.6% reo for high degree of restraint).
In summary the quantity of reo I have for flexure by itself is more than enough to handle the high degree of restraint for when shrinkage occurs.
The question is, should shrinkage reo be additive to the flexure reo? I was always led to believe that if you satisfy shrinkage with your flexure reo..."you're fine"... But I have my doubts.
Surely the mere action of shrinkage and the stiff columns means that tension builds up in the slab (ie so now we have the original flexure moment now with tension included). Does this exaserbate service cracking?