ASCE 7-05, 7.8 Roof Projections, says, "If the side of a roof projection is less than 15 ft. (4.6 m) long, a drift load is not required to be applied on that side."
See attached... [URL unfurl="true"]https://res.cloudinary.com/engineering-com/image/upload/v1480959017/tips/ASCE_7-05_7.8_Roof_Projections_wfubpp.pdf[/url]
I have a 450' x 330' roof with (30) Roof Top Units (RTU's) that are each 7'-4" x 14'-3" in plan dimension; 5'-0" high. The plan dimensions create a 16'-0" diagonal dimension, which, when viewed from a direction normal to the diagonal, would, thus, prompt the greater than 15'-0" requirement.
These RTU's are evenly and uniformly spaced 50', 75' or 100' o/c.
My typical practice would be to employ the conservative, safe route of applying the drift loads to each of these RTU's, even though each "side" is less than 15'-0". HOWEVER, I do NOT want to over-design and unnecessarily raise the cost. YET... Safety!
1. Would any of you consider the 15'-0" diagonal a justifiable "side"?
2. Is there a(n unpublished) concern for the multiple units which might induce the slightest turbulence or tunneling effects as implied by ASCE 7-05, 6.5.15.1 Rooftop Equipment, thereby justifying the snow drift application?
3. Would any of you ignore the drifts around the RTU's altogether?
Suggestions?
Thank you!
See attached... [URL unfurl="true"]https://res.cloudinary.com/engineering-com/image/upload/v1480959017/tips/ASCE_7-05_7.8_Roof_Projections_wfubpp.pdf[/url]
I have a 450' x 330' roof with (30) Roof Top Units (RTU's) that are each 7'-4" x 14'-3" in plan dimension; 5'-0" high. The plan dimensions create a 16'-0" diagonal dimension, which, when viewed from a direction normal to the diagonal, would, thus, prompt the greater than 15'-0" requirement.
These RTU's are evenly and uniformly spaced 50', 75' or 100' o/c.
My typical practice would be to employ the conservative, safe route of applying the drift loads to each of these RTU's, even though each "side" is less than 15'-0". HOWEVER, I do NOT want to over-design and unnecessarily raise the cost. YET... Safety!
1. Would any of you consider the 15'-0" diagonal a justifiable "side"?
2. Is there a(n unpublished) concern for the multiple units which might induce the slightest turbulence or tunneling effects as implied by ASCE 7-05, 6.5.15.1 Rooftop Equipment, thereby justifying the snow drift application?
3. Would any of you ignore the drifts around the RTU's altogether?
Suggestions?
Thank you!