- Jul 18, 2006
- 554
In ASCE 7-05 section 12.11.1, the out-of-plane forces for structural walls (shear and/or bearing) are 0.4SdsIWp with a minimum of 0.1Wp.
These forces are also used for anchoring or bracing the top and bottom of the the wall sections. A minimum anchorage load is given in section 12.11.2.
If a flexible diphragm is used for a C, D or E category building, the anchorage force doubles to 0.8SdsIWp (section 12.11.2.1). The code does not specifically state that the wall should be designed for out-of-plane forces (bending and shear) to this magnitude, only the anchorage.
Is this how you read it? Do you design the wall reinforcing and thickness for 0.4SdsIWp for all situations unless wind controls?
These forces are also used for anchoring or bracing the top and bottom of the the wall sections. A minimum anchorage load is given in section 12.11.2.
If a flexible diphragm is used for a C, D or E category building, the anchorage force doubles to 0.8SdsIWp (section 12.11.2.1). The code does not specifically state that the wall should be designed for out-of-plane forces (bending and shear) to this magnitude, only the anchorage.
Is this how you read it? Do you design the wall reinforcing and thickness for 0.4SdsIWp for all situations unless wind controls?