- May 12, 2014
- 1,700
When doing work south of the border, I've always used a factor of safety of 1.5 for overturning. The ASCE 7-16 load combination is 0.9D+1.0W for LSD (or 0.6D+0.6W for ASD). Am I allowed to satisfy these load cases with no additional factor of safety, i.e. is the load factor built into the calculation of wind loads? For comparison, the overturning load case in Canada is 0.9D+1.4W, which works out to a FOS of just over 1.5.