Warhamer

Structural
Jul 5, 2012
23
I have a question on ASTM E1300-12 Appendix X1. The question in specifics is in regards to the caution stated in X1.1.1 for using the alternative deflection calculation procedure, and pressures less then one-third design capacity of lite. Is someone able to provide some background on this caution statement or point me in the direction of which reference in the Standard I should pursue to get additional information on the caution statement?

Some Background information: Windows I usually work with are 24 to 36 inch base dimension, .25" thick. Generally the actual aspect ratio of the windows is between 1 and 2. The windows are being checked for wind loads only.

Thanks for your consideration and time.

EIT, Modular Building Industry
 
Replies continue below

Recommended for you

Warhamer,

Te reason for the caution in Appendix X1 about less than 1/3 of capacity is that the tables in E1300 are based on non-linear analysis. The glass gets stiffer as it deflects.
 
Glass99,

Thank you, Glass is not one of my normal materials. The PE I usually work with in regards to glass, had a medical event he has since recovered from.

EIT, Modular Building Industry
 