athomas236
Mechanical
- Jul 1, 2002
- 607
I am involved in a power and desalination plant that comprises 4 gas turbines and associated HRSGs supplying steam at 85bar 565C to 2 back pressure steam turbines through a HP steam header. Steam from the steam turbine exhausts is supplied at 3bar 160C to 5 desalination units through a LP steam header.
To accommodate for differences in the demand for power and water each HRSG is provided with a bypass valve which connects from HRSG outlet steam pipes (between the superheater outlet header and the boiler stop valve) to the LP steam header. There is an isolation valve in the pipework between the bypass valve and the LP steam header.
All pipework is designed in accordance with ASME B31.1 and this question relates to the interpretation of clause 122.5.1 of this code which states:
“Where pressure-reducing valves are used, one or more relief devices or safety valves shall be provided on the low pressure side of the system. Otherwise, the piping and equipment on the low pressure side of the system shall be designed to withstand the upstream design pressure. The relief or safety devices shall be located adjoining or as close as practical to the reducing valve. The combined relieving capacity provided shall be such that the design pressure of the low pressure system will not be exceeded if the reducing valve failed open”.
To meet the requirements of this the contractor is proposing the following:
(a) To install a safety valve on each bypass pipe between the bypass valve and the isolating valve. This safety valve is rated at 10% of the maximum bypass valve capacity and is intended to relieve any pressure caused by leakage through the closed bypass valve
(b) To install 3 pressure measurements on each bypass pipe between the bypass valve and the isolating valve. These pressure measurements will use a one out of three voting logic to close the bypass valve if pressures higher that the pipework design pressure are detected.
The bypass valves have hydraulic actuators designed to fail closed in the event of the loss of hydraulic actuation.
The contractor recognises that the capacity of safety valve does not meet the requirements of B31.1 but is arguing that the provision of 3 pressure measurements on each bypass pipe that will close the bypass valves meets the requirements for pressure relief devices as stated in clause 122.5.1. My own opinion is that this does not meet the requirements of this clause and that the only way to comply with this clause is to install safety valves or similar integrity mechanical pressure relief devices (bursting discs) rated for the maximum capacity of the bypass valves.
Any comments would be appreciated.
Best Regards
athomas236
To accommodate for differences in the demand for power and water each HRSG is provided with a bypass valve which connects from HRSG outlet steam pipes (between the superheater outlet header and the boiler stop valve) to the LP steam header. There is an isolation valve in the pipework between the bypass valve and the LP steam header.
All pipework is designed in accordance with ASME B31.1 and this question relates to the interpretation of clause 122.5.1 of this code which states:
“Where pressure-reducing valves are used, one or more relief devices or safety valves shall be provided on the low pressure side of the system. Otherwise, the piping and equipment on the low pressure side of the system shall be designed to withstand the upstream design pressure. The relief or safety devices shall be located adjoining or as close as practical to the reducing valve. The combined relieving capacity provided shall be such that the design pressure of the low pressure system will not be exceeded if the reducing valve failed open”.
To meet the requirements of this the contractor is proposing the following:
(a) To install a safety valve on each bypass pipe between the bypass valve and the isolating valve. This safety valve is rated at 10% of the maximum bypass valve capacity and is intended to relieve any pressure caused by leakage through the closed bypass valve
(b) To install 3 pressure measurements on each bypass pipe between the bypass valve and the isolating valve. These pressure measurements will use a one out of three voting logic to close the bypass valve if pressures higher that the pipework design pressure are detected.
The bypass valves have hydraulic actuators designed to fail closed in the event of the loss of hydraulic actuation.
The contractor recognises that the capacity of safety valve does not meet the requirements of B31.1 but is arguing that the provision of 3 pressure measurements on each bypass pipe that will close the bypass valves meets the requirements for pressure relief devices as stated in clause 122.5.1. My own opinion is that this does not meet the requirements of this clause and that the only way to comply with this clause is to install safety valves or similar integrity mechanical pressure relief devices (bursting discs) rated for the maximum capacity of the bypass valves.
Any comments would be appreciated.
Best Regards
athomas236