Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Tek-Tips community for having the most helpful posts in the forums last week. Way to Go!

Bad Power Factor Measurement

Status
Not open for further replies.

ENG2009

Electrical
Jun 12, 2009
9
0
0
US
I rented a Fluke 435 to measure the power consumption of some big power supplies we have (Input: 480VAC, 60 Amps). I logged the data on 3 different models of power supplies. On one of them the power factor was 0.71, but on the other two the results are meaningless - the power factor was around zero, it even went slightly negative. It really justs looks like noise around zero. The voltage and current readings seem fine. With a zero power factor, I can't really calculate my KW usage. Any idea why this would happen?

-Scott
 
Replies continue below

Recommended for you

What kind of load is it connected to? could it be something that could be distorting the waveform? digital meters can be flukey like that.
 
avogel may have a point about distortion. While this meter should be able to handle high THD voltage and current measurements, I see no reference in its specifications as to how it calculates PF, real and reactive power given non sinusoidal I and V inputs.
 
It's connected to a power supply about the size of a whole server rack. The power supply converts 480 VAC to 15 VDC 800 amps. I measured 3 different power supplies and it worked fine on the first. I don't think the other two are so different the meter would have a problem. I don't have the meter any more, so I can't redo it.

--Scott
 
If the supplies are similar (i.e. all SMPS with similar characteristics or all transformer/rectifier/big cap) then I'd expect the readings to be close. If one is a switcher with unity p.f. correction and the other two not, this could expose limitations in the meter's capabilities.

The only other thing to have checked (but if the meter is gone, its too late) is the possibility of an error in connecting the 3 Voltage and 3 current inputs. Getting two phases swapped or a CT connected backwards couuld account for weird settings.
 
Status
Not open for further replies.
Back