Indyhans:
I tend to agree with comments made by BIG H re the soft clay layer. Here are some of my comments.
It appears that you are building a wall that is vey high 50 ft at least based on the base width chosen or you are trying to invoke the lower stronger layers in your bearing capacity evaluation, or on the other hand you are concerned about settlement and have used a wider base. This has the effect of invoking characteristics of layers with depth, at least 1.5 times the footing width based on classical theory.
It may be that you are building an MSE wall, even so the base width suggests a tall wall.
Based on some quick calculations it would appear that if you do not want to remove the soft layer then your wall height for an FOS of 1.5 in BC would would have to be no greater than between 12 and 15 ft. and perhaps as low as 10 ft re BiGH's comments of the weak layer governing.
It is always of interest to see the variations one obtains using different equations in the literature and the uncertainty of which one to choose. That is the beauty about geotechnical engineering. Finally, you have to make the judgement call which ranges somewhere between optimistic and pesimistic values and invokes other concerns as well. Settlement issue could be a concern for both cantilever and MSE wall types. This has to be considered as well.
Removal of the weak layer is a solution if wall is to be much higher or other types of foundation improvement-short piles, stone columns, stone cement columns etc. The choice will depend on site factors/considerations.
![[cheers] [cheers] [cheers]](/data/assets/smilies/cheers.gif)