A homeowner wants to install an addition on the side of his house and he said he would like to bolt a double 2x10 beam to his existing stone foundation. The new floor joists will either sit on top of the beam or on joist hangers fastened on the beam.
According to my calcs the load on the beam will be 263 plf which equates to 100,000 lb-in (16' span). A double 2x10 beam can only support 41,200 lb-in. so the beam will obviously not work. A 2-ply lvl (11-7/8" deep and 16'6" long) can support 422 plf so this could be used.
My question is how do the bolts affect things? The bolts are securing the beam to the existing structure so do they need to be desinged to carry the 263 plf or is the beam still the controlling factor?
If my question is not clear let me know. Thanks.
According to my calcs the load on the beam will be 263 plf which equates to 100,000 lb-in (16' span). A double 2x10 beam can only support 41,200 lb-in. so the beam will obviously not work. A 2-ply lvl (11-7/8" deep and 16'6" long) can support 422 plf so this could be used.
My question is how do the bolts affect things? The bolts are securing the beam to the existing structure so do they need to be desinged to carry the 263 plf or is the beam still the controlling factor?