jittles
Structural
- Jun 6, 2011
- 174
I have a 6" total thickness slab over steel deck (4.5" concrete over 1.5" B deck) that has been designed for forklift loading. Following SDI's (Steel Deck Institute) guidelines, the deck is form-only and reinforcing has been provided to support the forklift loading.
The bottom rebar is intended to be in a low flute, with a little over 1" clear from deck to bar. The "d" depth of the bar is 4-1/2" from the top of the slab. Obviously this is my primary design concern - I want to maintain this effective depth.
At some locations, headed studs and spliced bottom bars result in the bars being pushed up against the side of the flutes (still maintaining the correct "d" depth and cover below), which means some of these bars no longer meet ACI clear cover of 3/4".
A couple of questions:
Is anybody aware of any guidance on bottom of deck clear cover for a slab on steel deck? ACI does not specifically address slabs on steel deck and SDI seemingly references ACI clear cover requirements, but they are clearly aimed at the clear cover to the top of the slab.
Are these bars still effective if they are up against (or very nearly up against) the side of a flute?
I'd appreciate any experience or code/standard references. I've reached out to SDI and am awaiting a response, but I thought I would ask here as well!
Thanks!
The bottom rebar is intended to be in a low flute, with a little over 1" clear from deck to bar. The "d" depth of the bar is 4-1/2" from the top of the slab. Obviously this is my primary design concern - I want to maintain this effective depth.
At some locations, headed studs and spliced bottom bars result in the bars being pushed up against the side of the flutes (still maintaining the correct "d" depth and cover below), which means some of these bars no longer meet ACI clear cover of 3/4".
A couple of questions:
Is anybody aware of any guidance on bottom of deck clear cover for a slab on steel deck? ACI does not specifically address slabs on steel deck and SDI seemingly references ACI clear cover requirements, but they are clearly aimed at the clear cover to the top of the slab.
Are these bars still effective if they are up against (or very nearly up against) the side of a flute?
I'd appreciate any experience or code/standard references. I've reached out to SDI and am awaiting a response, but I thought I would ask here as well!
Thanks!