Boys Home Fire Sprinkler Protection
FireProofDesign
We are in the process of fire sprinkler system design for a Boys Home. There are (5) individual buildings all around 1200 sq. ft. or less all typical housing construction. A Frame wood attics with 4 to 5 sleeping areas per unit. The local code (state) enforcement is looking for a full NFPA 13 system. The cost to the owner to fully protect the buildings with the required dry systems for the attics is too great. The building will fall under a R-2 construction type and should be classified as a 13R eliminating the need for attic protection. All occupants can self evac and the buildings are one story. Nevertheless the code enforcement is requiring a full 13 system. My question is IBC allows the use of draftstopping to eliminate protection and NFPA only has exceptions for fully insulating with non-combustible material. These are small attics has anyone encountered this any exceptions that are viable for NFPA 13 - fully blown insulation in the attics?
THANK YOU
NFPA 13 doesn't allow draft stopping to eliminate sprinkler protection. There are 3 ways I can think of in your situation and none are cheap:
1 - Fill entirely with non-combustible insulation.
2 - Utilize a UL Listed heat tracing
3 - Dry system
The dry system is likely the least expensive.
Travis Mack
MFP Design, LLC
"Follow" us at
What building code and edition has the ahj adopted?
So has anyone asked for a code reference requiring full 13 system?
AHJ is still under NFPA 13, 1999 - No code reference has been requested. It is a direct to owner job so no Architect on board and these are existing buildings.
Is this in a city or out in the boonies?
Woukd still ask the ahj where are they getting the full 13 from?
Is it an admendment? Is it because I want it??