serb
Electrical
- Oct 20, 2006
- 2
Elevator motor is fed through the controller, isolation transformer and disconnect switch in the elevator room. It's DC motor. Power source is in the load center and protection is done with 800A GE power circuit breaker equipped with SST trip unit. SST has rating 300A and is tapped at 225A for elevator protection. After eletrician pulled equipment grounding conductor between elevator controller and disconnect switch ground fault protection tripped the breaker in the load center. It's 3ph, 3w load center fed from transformer delta-star grounded. Ground fault settings is set for 0.6 at the SST unit.