I searched out a thread here that came very close to answering this question, but not quite. I hope you can provide a little more comment to this question.
We often design composite steel floor systems (also sometimes concrete on bar-joist floors)that have brick veneer clading on spandrel panels as the exterior skin. These spandrel panels are supported by the perimeter beams/girders, thus subject to the deflection of these members.
When limiting the deflection to L/600 or better, we typically consider the deflection caused by superimposed loads that would be felt by the spandrel. This would be the weight of the spandrel and any supported wall elements above (like windows), floor tributary live load, and miscellaneous superimposed floor tributary dead loads.
We typically do not consider the weight of the floor slab and beams since these are in place before the spandrel construction begins, and do not effect the deflection of the spandrel.
However, the Code simply says l/600 total load, which we have had others interpret to mean ALL loads need to be considered, not just superimposed. This can result in the need for very big beams, especially along the load bearing sides.
What are your interpretations and practices for this condition?
Thanks!
We often design composite steel floor systems (also sometimes concrete on bar-joist floors)that have brick veneer clading on spandrel panels as the exterior skin. These spandrel panels are supported by the perimeter beams/girders, thus subject to the deflection of these members.
When limiting the deflection to L/600 or better, we typically consider the deflection caused by superimposed loads that would be felt by the spandrel. This would be the weight of the spandrel and any supported wall elements above (like windows), floor tributary live load, and miscellaneous superimposed floor tributary dead loads.
We typically do not consider the weight of the floor slab and beams since these are in place before the spandrel construction begins, and do not effect the deflection of the spandrel.
However, the Code simply says l/600 total load, which we have had others interpret to mean ALL loads need to be considered, not just superimposed. This can result in the need for very big beams, especially along the load bearing sides.
What are your interpretations and practices for this condition?
Thanks!