When is it appropriate to use Clause 5.2.4 and figure 6 from BS 5628-3:2005, which relates to internal masonry walls that dont support imposed load.
Depending on the size and tickness of the wall, figure 6 tells you what restraint is needed to make the wall stable. However Cl.5.2.4 states that factors affecting stability should be accounted for in the design. This includes wind load.
Buildings have internal wind pressures thus internal walls will be subject to some lateral wind loading. Therefore do you have to check the wall as a panel subject to wind loading.
I know that an internal wall is not going to see much lateral load but it could get a bit every now an then. Its very unlikely that it will see 0.5q, where 0.5 is the net pressure coefficient for internal walls as given in the wind load code.
What do other engineers do in this case? Do you just satisfy the requirements of this clause or do you design it as a panel with some nominal lateral load? If you do this what coefficient do you apply to the dynamic pressure q? Or do you design it as a panel for a wind load of 0.5q?
Thanks for any comments
Depending on the size and tickness of the wall, figure 6 tells you what restraint is needed to make the wall stable. However Cl.5.2.4 states that factors affecting stability should be accounted for in the design. This includes wind load.
Buildings have internal wind pressures thus internal walls will be subject to some lateral wind loading. Therefore do you have to check the wall as a panel subject to wind loading.
I know that an internal wall is not going to see much lateral load but it could get a bit every now an then. Its very unlikely that it will see 0.5q, where 0.5 is the net pressure coefficient for internal walls as given in the wind load code.
What do other engineers do in this case? Do you just satisfy the requirements of this clause or do you design it as a panel with some nominal lateral load? If you do this what coefficient do you apply to the dynamic pressure q? Or do you design it as a panel for a wind load of 0.5q?
Thanks for any comments