dani864
Chemical
- Mar 8, 2007
- 4
We have a Zigzag transformer that had Bucholtz trip probably due problems on external line.
Immediately the customer takes DGA from bottom. The Hydrogen was 14 PPM and other gases also low. No C2H2, C2H4, 5 PPM.
Because this low values the transformer return to service and had another trip. Than it was moved to depot and opened. Inside the upper wood was broken and one of the coils was opened, but no electrical damage or burn signs.
The DGA from oil just before opening was 64 PPM H2 and no other gases more.
How it is possible that Bucholtz tripped from gases and in the same time or even 24 hours after it, they were not dissolved in oil, at least not in the bottom. Unfortunately the client not sample from the Bucholtz itself.
Thanks
Immediately the customer takes DGA from bottom. The Hydrogen was 14 PPM and other gases also low. No C2H2, C2H4, 5 PPM.
Because this low values the transformer return to service and had another trip. Than it was moved to depot and opened. Inside the upper wood was broken and one of the coils was opened, but no electrical damage or burn signs.
The DGA from oil just before opening was 64 PPM H2 and no other gases more.
How it is possible that Bucholtz tripped from gases and in the same time or even 24 hours after it, they were not dissolved in oil, at least not in the bottom. Unfortunately the client not sample from the Bucholtz itself.
Thanks