NickParker
Electrical
- Sep 1, 2017
- 420
In British Standards, the standards make ensure that the circuit breaker is selected such that it trips before the cable gets damaged. How this is ensured in NEC / IEC standards?
British Standard Cable sizing: (BS 7671)
Ib <= In <= Iz; and I2 <= 1.45 Iz
Iz - The current carrying capacity of the cable for the particular method of installation.
It - The tabulated current for a single circuit at an ambient temperature of 30°C.
Ib - The design current - the actual current to be carried by the cable.
In - The rating of the CPD, (Fuse or MCB).
British Standard Cable sizing: (BS 7671)
Ib <= In <= Iz; and I2 <= 1.45 Iz
Iz - The current carrying capacity of the cable for the particular method of installation.
It - The tabulated current for a single circuit at an ambient temperature of 30°C.
Ib - The design current - the actual current to be carried by the cable.
In - The rating of the CPD, (Fuse or MCB).