Bowin db
Electrical
- May 19, 2022
- 2
THANK you all for the kind replies. I am adding some additional information.
The sequence of power is as follows: City voltage 208-220v - 175A breaker - 175A shunt breaker (this is a breaker that has a secondary emergency feature called a shunt, ( I believe they are 120V normally open, when triggered they close the circuit sending 120V to the breaker and tripping it thereby killing the power to the motor. Next in line is the Isolation Transformer which cleans ( makes it that there are not high and low fluctuations to ) the current before it enters the main Control Unit. The control unit regulates the 220v motor (which was running but not in a consistent manner )
The Incoming volts from City 217,218,216 through Shunt Breaker (meaning tested each leg to neutral on the Load Side reading 123v, 94v, 216v Shouldn't it be the same voltage on either side of the breaker (high and low side) of the breaker? 2 of the 3 legs were losing voltage with no apparent load, though the load side of the breaker was still connected to the transformer and the shunt was still connected to the 110v supply.
This resulted in a blown transformer (where the coils on one of the 3 windings sparked and bulged out). Perhaps the Shunt (for some reason)was sending just enough to almost trip the breaker which reflected on the lower voltage reading on the load side.
Any comments would be greatly appreciated. The video would not upload so I attached Pics.
Here is a short video:
Thank you Bow
The sequence of power is as follows: City voltage 208-220v - 175A breaker - 175A shunt breaker (this is a breaker that has a secondary emergency feature called a shunt, ( I believe they are 120V normally open, when triggered they close the circuit sending 120V to the breaker and tripping it thereby killing the power to the motor. Next in line is the Isolation Transformer which cleans ( makes it that there are not high and low fluctuations to ) the current before it enters the main Control Unit. The control unit regulates the 220v motor (which was running but not in a consistent manner )
The Incoming volts from City 217,218,216 through Shunt Breaker (meaning tested each leg to neutral on the Load Side reading 123v, 94v, 216v Shouldn't it be the same voltage on either side of the breaker (high and low side) of the breaker? 2 of the 3 legs were losing voltage with no apparent load, though the load side of the breaker was still connected to the transformer and the shunt was still connected to the 110v supply.
This resulted in a blown transformer (where the coils on one of the 3 windings sparked and bulged out). Perhaps the Shunt (for some reason)was sending just enough to almost trip the breaker which reflected on the lower voltage reading on the load side.
Any comments would be greatly appreciated. The video would not upload so I attached Pics.
Here is a short video:
Thank you Bow