I am analyzing the attached detail. It is a cantilevered beam that is supporting the guide rail system for the roof of a structural steel building. As you can see, the cantilevered beam is connected to a perimeter beam of the building. This perimeter beam runs parallel to the open web steel joists and therefore isn’t supporting much roof load.
To withstand the moment applied at the cantilever beam to perimeter beam connection, I was thinking of welding the top and the bottom of the cantilever beam flanges to the web of the perimeter beam.
One thing I am concerned about is the web of the perimeter beam. I will check to make sure that the beam is able to resist the applied weak-axis moment, but are there other factors I should be considering when analyzing the web of the beam? I’ve also added a stiffener to help strengthen the web.
Any other feedback or suggestions for the detail would be appreciated.
Thank you.
To withstand the moment applied at the cantilever beam to perimeter beam connection, I was thinking of welding the top and the bottom of the cantilever beam flanges to the web of the perimeter beam.
One thing I am concerned about is the web of the perimeter beam. I will check to make sure that the beam is able to resist the applied weak-axis moment, but are there other factors I should be considering when analyzing the web of the beam? I’ve also added a stiffener to help strengthen the web.
Any other feedback or suggestions for the detail would be appreciated.