Cantilevered CMU Wall - Tension/Shear Interaction for Vertical Reinforcement?

Status
Not open for further replies.

EngineerEIT

Structural
Aug 31, 2015
29
I'm designing a cantilevered CMU wall (no soil retention) in a high wind region of the US. I've sized my reinforcement for the applied moment due to wind and then I started to think about shear transfer into the footing. Since this is not a load bearing wall, the contribution from friction is negligible and as far as I can see the only way to transfer shear would be through the vertical reinforcement.

I haven't seen any check like this for cantilevered retaining walls, am I missing something?

If so how would I do the check? ACI App D D.7.3?
 
Replies continue below

Recommended for you

I'd use the shear friction concept which will have the advantage that you'll be able to double count your flexural rebar as shear friction reinforcing.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
 