slickdeals
Structural
- Apr 8, 2006
- 2,266
I am designing a building that has a cantilevered roof over bleachers. The cantilever is about 25'. There are solid walls at the fixed end of the cantilever running perpendicular. There are 15' long return walls at the end of the perpendicular walls.
The cantilevered roof framing consists of tapered steel members with metal deck + topping spanning between them.
See attached sketch.
I am in Hurricane country (South Florida) with V=146 mph (HVHZ zones)
My questions are as follows:
1. Can Figure 6-18A be used with the assumption of obstructed wind flow (more than 50% blocked)? If so, does this CN value assume that there will be a stagnation pressure below the roof in addition to the uplift? If not, does the pressure calculated per 6.5.11.4.1 have to be added to this value?
2. As a secondary check, I am calculating the wind pressures (uplift) for this cantilevered roof considering it to be a partially enclosed building. This is for the case where the wind is blowing from left to right (in the cross section view).
3. Section 6.5.11.4.1 requires that roof overhangs be designed for a positive pressure on the bottom surface using a Cp = 0.80
Does this have to be in addition to any uplift calculated using Figures 6-6 through 6-10.
Any thoughts/suggestions on what sections of ASCE can be modified to apply to my situation?
As always, thanks.
We are Virginia Tech
Go HOKIES
The cantilevered roof framing consists of tapered steel members with metal deck + topping spanning between them.
See attached sketch.
I am in Hurricane country (South Florida) with V=146 mph (HVHZ zones)
My questions are as follows:
1. Can Figure 6-18A be used with the assumption of obstructed wind flow (more than 50% blocked)? If so, does this CN value assume that there will be a stagnation pressure below the roof in addition to the uplift? If not, does the pressure calculated per 6.5.11.4.1 have to be added to this value?
2. As a secondary check, I am calculating the wind pressures (uplift) for this cantilevered roof considering it to be a partially enclosed building. This is for the case where the wind is blowing from left to right (in the cross section view).
3. Section 6.5.11.4.1 requires that roof overhangs be designed for a positive pressure on the bottom surface using a Cp = 0.80
Does this have to be in addition to any uplift calculated using Figures 6-6 through 6-10.
Any thoughts/suggestions on what sections of ASCE can be modified to apply to my situation?
As always, thanks.
We are Virginia Tech
Go HOKIES