What would happen if a flash-over occurred within a section of GIS? Assuming worst case clearing time (1 cycle trip decision + breaker fail + backup breakers operating) how disastrous would it be? Or not much at all?
 
Theoretically, the pressure from the fault would cause one or more rupture discs to blow.

A few years ago I was commissioning an AIS ring bus with 345 kV SF6 breakers. All of our breakers were open. The remote end had energized the line and had soaked for about 5 minutes. I went outside to check the voltages at the CCVT & VT box for the line and we heard what sounded like a flag pole "clanking". My CCVT voltages disappeared. The CCVT/VT secondary boxes were about 12 feet from the failed breaker.

The center phase had flashed over phase to ground. Fault records from the remote end (about 1 mi away) indicted ~28kA, with ~ 3cycle clearing time (411L relays, 2 cycle breakers). Locally, some reported seeing the center phase of the line gallop. The voltage dip was so pronounced that a large automotive plant across the way tripped off line (fed from 138kV).

After verifying that my underwear was clean, I inspected the GCB. The rupture disc was intact, with no visible damage to the GCB. Compared to the other phases, the cement pad appeared darker, which we speculated was due to exterior moisture on the tank being thrown off from the forces of the fault. An SF6 sample was drawn with about 200 ppm SO2.

The OEM replaced the failed phase and took the failed unit to the factory for analysis. About eight months and 15 emails asking for the analysis, the OEM reported internal contamination as the root cause. These particular type of breakers are shipped from the factory with the bushings installed and a small positive SF6 pressure. FWIW, Doble tests were performed on each breaker as part of the commissioning tests and the results from this breaker were no different than the sister units.
 
In the least, your story is comforting lol. :)
 
Now, THAT's a good story. And well told. I stay away from those things. 690 V is enough for my body (and soul).

Gunnar Englund
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.
 
Being able to put your hand on an aluminium tube and being 6" from a quarter million volt busbar is unnerving.

I used to hate being in the breaker hall when our generators closed onto the system because if something was going to go wrong that was probably when it was going to happen. The day one of the shift managers manually closed a machine onto the bar about 40° out of phase scared the, ahem, poop out of me. That's nearly 3 o'clock on the synchroscope, after we'd talked about how we'd close just before twelve o'clock with the machine running slightly fast. The auto-synchroniser and checksync relays were both out, and we were closing up the old way. Not something many of us had done a manual sync 'for real', and this guy had never done it before:

"Close! Close!"
"When, now? Oh, OK"
"No, wait. No! NO!! F--k!"

Apparently the angry growl I heard in the breaker hall - and which seemed to lasted *forever* - was nowhere near as scary as being on the machine floor where the whole turbo-generator train rocked on its foundations. Some old hands came down white as ghosts after that.
 
I remember now. Summer job in a hydroelectric 3x40 MVA station. Midsummer. That is sacred in Sweden. And there I was "assistant control room assistent" - which meant reading water level and feeding pig's ears with white fat worms to the German Shepheard that was our defence against sabotage). So, being the youngest, I got a short training in how to synch the units before the guys went off with "gals and bottles". But they forgot to tell me about the slow motor mechanism (no air, no springs, just a motor and a gear that took the breaker above the trip point. It took several seconds from ON until the breaker closed. When the scope was at noon, I pressed the button and it wasn't until six P.M. that I heard the bang.

Turned out to be a much better time than 3 o'clock. That would have caused mechanical damage. But now, we had lots of current but not much forces.


Gunnar Englund
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.
 
In the event of  internal flash-over occurred within a section of GIS the following potential issues should be considered:
. a)High frequency fast transient overvoltage could be caused unexpected failure on the insulation of other equipment connected to it and the grounding system.
. b) Gas overpressure can damage the vessel, rupture disk or other internal components of the GIS.
. c) If the GIS is installed indoor, there is a risk that the overpressure damage the building


Adding special pressure relieve louvers, could mitigate the potential damages to building and personnel For additional information in this matter, see the excerpt below from typical installation in 15 GIS substations for a client in the US.

GIS_-_Pressure_Relief_Louver_kqdet1.jpg
 
Awesome! Can you increase the pic in size, its blurry on my end.
 
Thank you- again. :)


Can such a blast injure someone from over pressurization of the room? Even with vents?


 
Although the blast effect of sudden release overpressure has been some incident it is a rare event, however, there is potential for injury. Should be noted that there is no known injuries incident due to blast wave effect.
Injuries are a function of the levels of protection stand-off distance and predicting blast effects. Specific blast design concerns and mitigation options should be evaluated on a case by case basis for GIS project.
Will be prudent to take certain precautions and evaluate the probability of this type of fault and the consequences associated with this event.
 
Like tripping on low-low lol...


Hope it never happens outside of that.
 
Have seen burn-through of bus duct, along with deposition of a highly corrosive white powder, presumably hydrogen fluoride crystals; off-potential-only haz-mat clean-up of switchgear externals without violating limits of approach was the first step so that isolation and establishment of work protection could be undertaken, following which necessary dismantling and final clean-up could be undertaken. Once chemical hazards were eliminated, the usual assessment, ordering / acquisition of parts leading to repair / replacement took place, along with a more detailed fault analysis.

CR

"As iron sharpens iron, so one person sharpens another." [Proverbs 27:17, NIV]
 
Was this SF6? (I'm thinking something like GITL, so forgive me if you had classical bus duct in mind) What was the cause of failure?
 
Yes, classic SF6 switchgear; free dancing metallic particle contamination leading to PD as per cuky's description.

CR

"As iron sharpens iron, so one person sharpens another." [Proverbs 27:17, NIV]
 
How do hydrogen fluoride crystals form?
 
I'm not a chemist, but I've been told it's something to do with very high levels of energy dissociating the SF6 just as it's vented to the atmosphere. Reportedly the fluorine has a high affinity for the hydrogen found in water vapour, which it will dissociate to get the H needed to yield HF and free O2.

Some of the energetic sulphur may also combine with hydrogen to yield H2S; maintenance people attending to faulted SF6 switchgear have reported both the white powder and the smell of rotten eggs.

CR

"As iron sharpens iron, so one person sharpens another." [Proverbs 27:17, NIV]
 
I've heard that the byproducts or SF6 after it extinguishes an arc are toxic, but don't know to that degree.


How toxic are the crystals btw?
 
I don't know the answer to that.

CR

"As iron sharpens iron, so one person sharpens another." [Proverbs 27:17, NIV]
 