caterpillar voltage control problems

Status
Not open for further replies.

loopierxp

Electrical
Sep 23, 2012
2
Hi everyone! I am new here and having some problems. I have been working on a caterpillar sr4 99kw generator. It was equipped with a vr3 auto regulator which went out. I replaced the vr3 with a vr6 and the generator works fine in auto but when I switch to manual it pops the 12 amp fuse on the front of the caterpillar 7c-2700 manual voltage controller. When switched back to auto it would then spike over 600 volts (480 volt system) so I shut the regulator off. Thinking it was a bad manual controller I replaced the 7c-2700 with a basler mvc300 and encountered the same problems. My sensing voltages are rock solid at 240vac and my excitation voltage sits at approximately 10.8-11vdc with about a 2.5 amp draw. I am stumped with this one. Any help would be greatly appreciated. Thanks in advance.
 
Replies continue below

Recommended for you

You need to use the Basler MVC112 Manujal Voltage Control, use the Basler AVC 63-12 manual, publication number 9337200991F for reference.

Here is the link to the correct manual voltage control module,


As I remember (sorry, been awhile since doing this last) the difference is a freewheeling diode in the field circuit that prevents the VR6 from seeing an open field condition during switchover, also some additional circuitry to better manage power for excitation when using a static excited generator, at 99 kW I'm assuming you do not have a PM, correct?

Anyway, hope that helps,

Mike L.
 
Thats correct. No permanent magnet. I will look into trying the mvc112. Thanks for the input.
 