Recently, while performing a reactive test on our generator, our 40-2 loss of excitation relay tripped before we reached our generator capability curve. We backed off the MVAR, the relay cleared. We increased the MVA, and the relay tripped again at approximately the same point (0.828 pu). This relay is an old Westinghouse KLF distance relay.
We checked the calibration on the relay, and it checked good at 2.07pu. We checked four points on the curve, and the circle appears to be circular and centered on the y axis. At the time, I did not think to input the conditions which caused the trip.
If the relay calibrated good, and the mho circle is circular, what else could cause the relay to trip incorrectly? What could we check?
We checked the calibration on the relay, and it checked good at 2.07pu. We checked four points on the curve, and the circle appears to be circular and centered on the y axis. At the time, I did not think to input the conditions which caused the trip.
If the relay calibrated good, and the mho circle is circular, what else could cause the relay to trip incorrectly? What could we check?