I am investigating three treated water pumps (in the same installation) that have experienced significant cavitation damage to the pump casing on the suction side. The pumps typically operate with about 8m NPSH, have a cast iron casing and bronze impeller. There is no noticable cavitation damage to the impeller.
The pumps are conventional dual-suction split casing centrifugal water pumps from a reputable manufacturer. The inlet conditions are not the best, with three 90-degree bends (in the same direction) in quick succession leading to the pumps. Individually, the pumps are operating at about 500L/s at 30m head.
The pumps are operating at a specific speed (in US units) of approximately 3000, and a suction-specific speed of around 8000.
My initial thoughts are that this is due to a combination of the relatively high suction-specific speed combined with the poor inlet conditions, but I am puzzled by the fact that there is damage to the casing but not the impeller.
Any thoughts?
The pumps are conventional dual-suction split casing centrifugal water pumps from a reputable manufacturer. The inlet conditions are not the best, with three 90-degree bends (in the same direction) in quick succession leading to the pumps. Individually, the pumps are operating at about 500L/s at 30m head.