pioneer09
Structural
- Nov 7, 2012
- 67
Are there any published values for Cee & Zee sections used as purlins when attached to standing seam roofs. Per AISI, there is a reduction factor determined in accordance with AISI S908 that is to be used. I would think pre-engineered metal building companies either have their systems tested or utilize their own derived/calculated values. From past experience, I have typically seen values in the range of R=.6-.7
Wondering what others are using when testing/resources that the metal building companies have are not available.
Wondering what others are using when testing/resources that the metal building companies have are not available.