afzumannu
Electrical
- Jul 1, 2011
- 93
Dear All,
We Have 33 KV filter bank circuit for Compensation plant which include Line CT, Reactor and capacitors bank, we are facing trouble as this one phase circuit is tripping with Thermal protection and others are Ok, reactor value 11.85mH, Line CT 1000/1, Unbalance CT 10/5 CPR-04 relay is used for Protection, CT checked it's fine, Capacitors bank checked it's fine too, all the balance value and similar, capacitor in double star connection. We have doubt in reactor unit as it producing abnormal sound as we have noticed during switching ON,we dont have any testing kit for its mH value checking or any other test, can somebody help me out that how to test or check this reactor by simple method that it is ok or not? I am attaching SLD of one phase.
We Have 33 KV filter bank circuit for Compensation plant which include Line CT, Reactor and capacitors bank, we are facing trouble as this one phase circuit is tripping with Thermal protection and others are Ok, reactor value 11.85mH, Line CT 1000/1, Unbalance CT 10/5 CPR-04 relay is used for Protection, CT checked it's fine, Capacitors bank checked it's fine too, all the balance value and similar, capacitor in double star connection. We have doubt in reactor unit as it producing abnormal sound as we have noticed during switching ON,we dont have any testing kit for its mH value checking or any other test, can somebody help me out that how to test or check this reactor by simple method that it is ok or not? I am attaching SLD of one phase.