I’m trying to come to a conclusion on code requirements as they pertain to bolt-on gasketed saddles for hot tapping in a chilled water system. Ultimately, I’m questioning if they are allowed by code?
My present point of view:
From ASME B31.9-2008, 904.3.1:
…branch connections may be made by any of the following methods:
(a) Fittings. Tees, extruded outlets, laterals, crosses, etc., manufactured in accordance with a standard listed in Table 926.1.
(b) Outlet Fittings. Cast or forged, integrally reinforced, welding outlet fittings, nozzles, forged couplings, and similar items, attached to the main by welding.
(c) Direct Connection to the main. Welding the branch pipe directly to the main, with or without added reinforcement, as shown in details of branch connections in Figs. 927.4.6-1 and 927.4.6-2 and the rules of para. 904.3.2.
(d) Mechanically Formed Tee Connections in Copper Tube. See para. 930.2.
None of the bolt-on tapping fitting assemblies I’ve seen are manufactured to a standard listed in the referenced table. Therefore, my present conclusion is that these types of fittings do not meet code requirements.
Does anyone care to shed some light regarding the use of these fittings or code interpretation?
My present point of view:
From ASME B31.9-2008, 904.3.1:
…branch connections may be made by any of the following methods:
(a) Fittings. Tees, extruded outlets, laterals, crosses, etc., manufactured in accordance with a standard listed in Table 926.1.
(b) Outlet Fittings. Cast or forged, integrally reinforced, welding outlet fittings, nozzles, forged couplings, and similar items, attached to the main by welding.
(c) Direct Connection to the main. Welding the branch pipe directly to the main, with or without added reinforcement, as shown in details of branch connections in Figs. 927.4.6-1 and 927.4.6-2 and the rules of para. 904.3.2.
(d) Mechanically Formed Tee Connections in Copper Tube. See para. 930.2.
None of the bolt-on tapping fitting assemblies I’ve seen are manufactured to a standard listed in the referenced table. Therefore, my present conclusion is that these types of fittings do not meet code requirements.
Does anyone care to shed some light regarding the use of these fittings or code interpretation?