I am developing a water treatment system for a operation that is not unlike a brewery, as we are settling, neutralizing, and discharging high solids fermentation effluent once it has been physically dewatered. I will likely be designing a circular cone-bottom clarifier specifically for this application, and would appreciate any guidance from operators or engineers with knowledge and/or experience on the draining of clarified effluent. Any feedback on the validity of the below statements or the scenario in the last paragraph would be appreciated. Thanks in advanced for any clarification (doh!).
Numbers and configuration matter here so here is the set up:
1. Effluent has 1 percent solids going into the clarifier.
2. After a 3-4 hour primary sedimentation, the contents of the clarifier are pumped to a continuous-flow neutralization system, adding hydrated lime at a minimum of 20 GPM.
3. A secondary clarifier will be paced after neutralization, as hydrated lime also has some coagulating properties and may facilitate further TSS and BOD removal.
4. Both clarifiers would have at least 45 degree slanted cone bottoms. They would be sized for roughly 800 gallons, with a height:diameter ratio between 1:1 and 1.5:1. I am basing this on the specs of industrial clarifiers that are available online.
5. The first clarifier would have a drainage port on the front of the tank, position near the bottom of the cylinder. This is distinct from the sludge port at the bottom of the cone, which is used to pump out sludge.
Specifically, I have been unable to find reliable design resources for the selection of hardware fittings and appropriate drain height that will remove clarified effluent without excluding a majority of the water below the drainage level. A drainage port that is connected to a vertical open pipe on the tanks interior may be the most obvious solution, but not necessarily the best. The ideal would be a drainage system that allows for the extraction of water from multiple heights, but can be configured on smaller industrial plastic tanks.