Classifications for Reinforcing Bars - Eurocode vs ACI
GEE8B
Hi all.
in Eurocode, reinforcement for concrete is classified in three groups (A, B, and C), each having a characteristic minimum tensile to yield ratio and an accompanying minimum tensile strain (measured at ultimate, i.e., the highest point on the stress-strain curve). The various available reinforcement materials are then certified to conform to these classifications, in turn defining their respective ductilities and shaping how they are allowed to be used in the design of structural elements. It is all quite intuitive.
In contrast, ACI 318 doesn’t really do this. ACI says nothing about uniform strain (i.e., strain measured at max tensile stress). Instead of having strain-based reinforcement categories, ACI 318 states which reinforcement type (as characterized by an ASTM designation) is acceptable for which structural application/usage. It works, but it just feels like there is a grey area.
When we do design by ACI here in the states, determination of tensile strain is a key step in defining whether the section qualifies as tension-controlled vs. compression-controlled or transnational, and this feeds into the phi factor used to calculate capacity. It isn’t unheard of for calculated (theoretical) tensile strains to get up into and sometimes beyond the 5% range (0.05 in/in) when doing design by ACI 318, but how do we know the reinforcement material itself, as characterized by ASTM / ACI, can actually achieve these tensile strains? Shouldn’t there be a manufacturing requirement that ensures material is meeting a certain uniform strain threshold?
I don’t doubt that most of these commonly available steel reinforcements have some internal data showing that theoretical uniform strains are being achieved (stress-strain curves would obviously show it), and I’ve seen stress-strain curves that can provide some comfort on this front. But my issue is that there is no formality to it. All that we see published in the ASTM specs (for example, A706 and A615) is a minimum elongation on a predetermined gage length measured at fracture. Yet strain at fracture is an utterly pointless attribute when it comes to engineering design of reinforced concrete.
Would ACI benefit from categorizing steels based on a formal ductility classification (as Eurocode does)?
Would love to hear your thoughts on this.
Pls look ACI 318-19 relevant clauses at CHAPTER 20—STEEL REINFORCEMENT PROPERTIES
Copy and paste of the relevant table excerpt ,
I cannot give you the formula for success, but I can give you the formula for failure..It is: Try to please everybody.
Thanks HTURKAK. I overlooked the uniform elongation requirement for A706 bar established in ACI318.
The fact remains that A615 bars, as well as other non-A706 reinforcements, have no definition for uniform elongation, yet are broadly accepted and specified in numerous structural applications.
Ductility and the expectation for reliable inelastic behavior beyond yield is not an attribute that is exclusive to seismic design. It seems odd to me that other than for A706 bars, the matter of minimum uniform elongation isn’t clearly defined by ACI 318.
It appears the elongation limits for A706 reinforcing in ACI are different than in the ASTM spec. Presumably, the elongation limits for A615 reinforcing in the ASTM spec are considered adequate for the design application for which they're specified. Interestingly, the minimum elongation values for A706 bars in ACI table posted are lower than what's in the ASTM A706 spec, but similar to A615.
BridgeSmith-
Correct. I believe the elongations listed in the ASTM spec for A706 and for A615 are “total elongations”, which coincide with fracture of the bar. As mentioned above, this isn’t a very valuable attribute from an engineering design standpoint, at least not compared to uniform elongation.
The latest version of ASTM A706 (22a) actually includes a supplement outlining some uniform elongation information, but seems to reference this to use for high seismic applications.
So in my view, still a grey area. Would just seem a lot simpler and more transparent for the design code (i.e., ACI 318) to establish ductility classes of reinforcement (with characteristic T/Y and uniform elongation values), and then let the manufacturers produce material as they see fit in order to align with the established classes.