DM2222
Structural
- Sep 24, 2013
- 11
I am curious to get a few opinions on an issue I have run into:
I like to provide control joints in CMU per the NCMA recommendations, and am typically able to do so with most buildings. I have run into a residential application with lots of openings. I am in a Seismic Category "C" with high winds as well. The shearwalls have been a challenge, and there just flat isn't a suitable place for a control joint in a few directions. I had to coax the architect into some reduced openings in several locations to make the lateral design work. The lintel reinforcement is required to extend 24" past the openings, so this means a control joint adjacent to an opening would reduce the shearwall length by 24" (on each end in many cases), and I just can't give up the shearwall.
What I have decided to do, is to heavily reinforce the wall horizontally in accordance with the NCMA TEK 10-3 which prescribes a minimum horizontal reinforcement that allows for control joints to be omitted entirely. Unfortunately, I don't see many other options, but I just hate to vary from what I am used to. Structurally, I am okay with this, but I do fear that there may be objectionable cracking in the finish stucco coat that will cause fingers to be pointed at me. At the end of the day, I don't know if we will have a major earthquake, but I KNOW the wall will shrink. So a couple questions:
1. Has anyone had success omitting CJ's by reinforcing heavily? (requires area of horizontal steel = .002*An)
2. I have seen many people that still put a CJ, but run all the horizontal reinforcing through. This seems like it would not be effective as a CJ, but does anyone follow this practice with success?
3. I also hear of folks not reinforcing per TEK 10-3, and ignoring the need for control joints (with purported success). Anbody in this category?
4. At the end of the day, do you say: small shrinkage cracks aren't structural and structural concerns trump aesthetic shrinkage cracks and roll on?
5. Anybody have a magic bullet, awesome structural note, or waiver that will let the shearwalls work, eliminate all cracking and help me sleep well?
6. What would you do?
Thanks for anyone's time and input!
I like to provide control joints in CMU per the NCMA recommendations, and am typically able to do so with most buildings. I have run into a residential application with lots of openings. I am in a Seismic Category "C" with high winds as well. The shearwalls have been a challenge, and there just flat isn't a suitable place for a control joint in a few directions. I had to coax the architect into some reduced openings in several locations to make the lateral design work. The lintel reinforcement is required to extend 24" past the openings, so this means a control joint adjacent to an opening would reduce the shearwall length by 24" (on each end in many cases), and I just can't give up the shearwall.
What I have decided to do, is to heavily reinforce the wall horizontally in accordance with the NCMA TEK 10-3 which prescribes a minimum horizontal reinforcement that allows for control joints to be omitted entirely. Unfortunately, I don't see many other options, but I just hate to vary from what I am used to. Structurally, I am okay with this, but I do fear that there may be objectionable cracking in the finish stucco coat that will cause fingers to be pointed at me. At the end of the day, I don't know if we will have a major earthquake, but I KNOW the wall will shrink. So a couple questions:
1. Has anyone had success omitting CJ's by reinforcing heavily? (requires area of horizontal steel = .002*An)
2. I have seen many people that still put a CJ, but run all the horizontal reinforcing through. This seems like it would not be effective as a CJ, but does anyone follow this practice with success?
3. I also hear of folks not reinforcing per TEK 10-3, and ignoring the need for control joints (with purported success). Anbody in this category?
4. At the end of the day, do you say: small shrinkage cracks aren't structural and structural concerns trump aesthetic shrinkage cracks and roll on?
5. Anybody have a magic bullet, awesome structural note, or waiver that will let the shearwalls work, eliminate all cracking and help me sleep well?
6. What would you do?
Thanks for anyone's time and input!