Code specified minimum rerinforcement for retaining walls?

Status
Not open for further replies.

Prestressed Guy

Structural
May 11, 2007
390
Is there a code specified minimum reinforcement ρ for retaining walls for the toe and heel reinforcement as well as the vertical bars. In section 14.3.2 ρ[sub]v[/sub]is listed as 0.0012 for #5 and smaller but is this only for above grade walls? I know that it would also need to meet the 200*b*d/F[sub]y[/sub] for minimum bending reinforcement to insure a ductile break but is there another limit?
 
Replies continue below

Recommended for you

ACI section 10.5.4 covers footings and minimum area of steel.

For a joy ride and lots of fun - review this: thread507-343576


Check out Eng-Tips Forum's Policies here:
faq731-376
 
Worth pointing out that in 318-14 (section 8.6.1.1), ACI clarifies the provision under debate in that thread, and states in the commentary that Asmin should be placed entirely in the tension face.

Brian C Potter, PE
Simple Supports - Back at it again with the engineering blog.
 
The retaining wall is a flexural member and needs that level of minimum reinforcement. So at least one way slab minimum reinforcement in any face that can be in tension.
 