Hello All,
I have a question with many potential answers and I'd like to get any opinions that I can. I have a situation where a corner office is reporting that it is continuously too cold.
First off the climate is Canada, so our winter design temp is usually -40deg (C or F). The office is supplied ventilation air from an air handling unit that supplies tempered air to all the offices in that wing. The heating for the particular office comes from a fan-powered terminal unit with an electric coil. The room is around 65 square feet (6.04 m2), two windows 8 ft2 each(double paned, argon filled) facing east and south. It is ground floor, slab on grade, conditioned spaces above and on two sides. Wall construction is R20. Dimensions are W- 19.5 ft (5.96 m) L – 12.95 ft (3.95 m) H- 10.8 ft (3.28 m).
The terminal unit varies the tempered air (which is used for cooling in the summer and ventilation only in the winter) with a modulating damper. In the winter the damper closes to min position. At this point a call for heat will energize the fan in the terminal unit and energize the heating coil (single stage). The terminal unit then recirculates air in the space while adding a small amount of ventilation air.
The reason I'm asking the question is that there is no good reason for this room to be cold. The terminal unit provides 200 cfm (95 l/s) of air, and the electric coil is 2.5 kW (8530 Btu/hr). This means that we have over 130 (Btu/hr)/ft2 of heating (414 W/m2).
Does anyone have any thoughts on the matter? I've already examined a dozen possibilities, but I'd like to see if anyone could think of anything that I can't. The installation contractor, the controls contractor and the unit manufacturer have all inspected the situation and say that the system is working as designed, and that the design is to blame…I disagree.
Any thoughts?
I have a question with many potential answers and I'd like to get any opinions that I can. I have a situation where a corner office is reporting that it is continuously too cold.
First off the climate is Canada, so our winter design temp is usually -40deg (C or F). The office is supplied ventilation air from an air handling unit that supplies tempered air to all the offices in that wing. The heating for the particular office comes from a fan-powered terminal unit with an electric coil. The room is around 65 square feet (6.04 m2), two windows 8 ft2 each(double paned, argon filled) facing east and south. It is ground floor, slab on grade, conditioned spaces above and on two sides. Wall construction is R20. Dimensions are W- 19.5 ft (5.96 m) L – 12.95 ft (3.95 m) H- 10.8 ft (3.28 m).
The terminal unit varies the tempered air (which is used for cooling in the summer and ventilation only in the winter) with a modulating damper. In the winter the damper closes to min position. At this point a call for heat will energize the fan in the terminal unit and energize the heating coil (single stage). The terminal unit then recirculates air in the space while adding a small amount of ventilation air.
The reason I'm asking the question is that there is no good reason for this room to be cold. The terminal unit provides 200 cfm (95 l/s) of air, and the electric coil is 2.5 kW (8530 Btu/hr). This means that we have over 130 (Btu/hr)/ft2 of heating (414 W/m2).
Does anyone have any thoughts on the matter? I've already examined a dozen possibilities, but I'd like to see if anyone could think of anything that I can't. The installation contractor, the controls contractor and the unit manufacturer have all inspected the situation and say that the system is working as designed, and that the design is to blame…I disagree.
Any thoughts?