I have found that manufacturers torque recommendations are a perfect solution in a perfect world. Unfortunately we live in the real world.
If anyone wants to get their hands dirty try this:
Install a #6 AWG seven strand cable in a set screw terminal. Use recommended torque.
Give the cable a slight twist in the direction to unlay the stranding.
Drop the cable out of the terminal.
Test two:
Install a new piece of cable and over torque it to a ridiculous extreme.
Give the cable a slight twist and drop it out of the terminal.
The manufacturers torque recommendation is great if the cable is never touched in any way forever after installation.
Don't think of moving the cable so as to be able to measure the current with a clamp on ammeter.
I have encountered many installations where heat damage of one type or another was done as a result of a connection that was probably up to spec when installed but then became loose.
One instance was a 1200 amp switch that was destroyed due to heating that started in the connections.
Recommendations:
1> Tighten the terminal.
2> Twist the cable back and forth as much as possible.
3> Retighten. The screw will now turn easily from 1/4 to 1/2 turn.
Repeat until the screw stays tight.
Exceptions:
Some compacted strand cables will stay tight the first time.
This is for copper. For aluminum conductors in sizes from #14 AWG to about # 8 AWG don't try to put the conductor under a screw type terminal. Use a suitable connector to connect a copper pigtail to the end of the aluminum and connect the copper as you would do normally.
How to connect the pigtail?
There are some excelent connectors on this page for smaller sizes.
There appears to be only one connector still listed for cu/al. and it may not be large enough.
The Twister Al/Cu
In years past I have had excellent results using either Wing Nuts or B-Caps with aluminum. Unfortunately these are no longer listed for Al. If you do use them, fill them with a corrosion inhibitor such as Penetrox or No-Alox. After connecting the wire wipe off the excess grease and tape well to prevent the grease from weeping.
For aluminum (and copper connections that may be subject to load cycling) look for:
Live-action, square-wire spring
in the specs.
Avoid connectors with
Fixed, Square-wire spring
for aluminum use.
For larger sizes consider a butt splice. Burndy has a good selection of Cu/Al rated butt spices.
Go here and drill down:
Search on this number for an example:
YSU4W8W
Good luck.
Bill
--------------------
"Why not the best?"
Jimmy Carter