Coldform / Gypsum Shear Wall

Status
Not open for further replies.

cal91

Structural
Apr 18, 2016
294
0
0
US
I've got a storage unit project using coldform framing. The exterior walls will be a typical coldform shearwall with gauge steel siding. However, the interior walls which I rely upon for shear, will only have 5/8" gyp board on both sides and no steel siding.

Do I need to use and R value of 2 instead of an R value of 6.5 ?! If so I'll need to put steel siding in all the interior walls. I'm hoping there's a way around this.
 
Replies continue below

Recommended for you

ANSI 400 has provisions for it. But I can't make it work with a R value of 2 anyways... looks like i'll have to throw steel siding into the interior walls.
 
XR250 said:
You could also strap brace it. Might be cheaper overall than the other alternatives.

What do you use for the flat straps? CS/CMST coiled straps? I'm wondering about holes in the straps because Fu*An must be greater than Fy*Ag
 
Have not done one in awhile but I never spec'd coiled strap as the loads were generally too high. I believe most of mine were 3 or 4" wide, 14ga strap that was made up by a sheet metal fabricator.
You would have to check the strap for reduced area from the holes, but in my experience, the ability to get enough fasteners in the strap was the limiting factor.
 
I second the use of flat strap bracing if you can make it work. Sureboard is great structurally but we get lots of complaints about it being costly and difficult to work with. This tech brief is a great introduction to cold-formed shearwalls and strap braced walls (Link).
 