What is the standard approach when detailing columns (which have unbalanced moments) and stop at the roof of a flat slab? For example, I have a 30' span next to a 18' span and the unbalanced moment is being resisted by the column. However, due to the slab being fairly thin, I cannot realistically develop any bars larger than #6/#7 in the slab.
Is it appropriate to assume that this column is "cracked" or to be a pinned joint for column design? The slab will be designed assuming unbalanced moments from the slab are being transferred into the column to preclude punching shear failure prior to redistribution. Also additional bottom reinforcement will be provided in the span to account for moment redistribution.
Would like to hear your thoughts.
Is it appropriate to assume that this column is "cracked" or to be a pinned joint for column design? The slab will be designed assuming unbalanced moments from the slab are being transferred into the column to preclude punching shear failure prior to redistribution. Also additional bottom reinforcement will be provided in the span to account for moment redistribution.
Would like to hear your thoughts.