I'm looking at analysis performed by an engineer no longer with the company and I'm concerned that it's incorrect but I'm not confident enough to push the issue. I'd appreciate any input.
Structure consists of two 20-ft sections of 8-in pipe bolted together through 1-in flanges. Top section is sch 40, bottom is sch 80.
Loading is from an FM antenna array and windloads (approx 2 kip compression/30 ft-kip moment at base).
He disregarded compression and treated the whole thing as a simple Mc/I bending problem saying that it's OK because ó < Sy.
However, when I follow AISC Manual of Steel Construction approach for combined column loading, looking just at the lower sch 80 section, I find the eqns in sec'n H are > 1 which says the design is insufficient.
The reason for my lack of confidence is that the axial stress is only about 0.2 ksi which seems to say this thing is basically a vertical cantilever beam in bending so Mc/I approach is right.
I'm losing sleep over this and any help would be greatly appreciated.
Thanks!
Structure consists of two 20-ft sections of 8-in pipe bolted together through 1-in flanges. Top section is sch 40, bottom is sch 80.
Loading is from an FM antenna array and windloads (approx 2 kip compression/30 ft-kip moment at base).
He disregarded compression and treated the whole thing as a simple Mc/I bending problem saying that it's OK because ó < Sy.
However, when I follow AISC Manual of Steel Construction approach for combined column loading, looking just at the lower sch 80 section, I find the eqns in sec'n H are > 1 which says the design is insufficient.
The reason for my lack of confidence is that the axial stress is only about 0.2 ksi which seems to say this thing is basically a vertical cantilever beam in bending so Mc/I approach is right.
I'm losing sleep over this and any help would be greatly appreciated.
Thanks!