It has been a long while since I have been in this forum. Hello everyone.

I want to pick everyone’s brain here.

I have been called, of course after the fact, to evaluate a situation where a contractor has already installed a beam, 9.33’ span made up from SYP number 2. The beam is supporting 5 roof trusses, and it is already loaded. See the attached simple and NTS section.

The contractor and the owner are not for removing and replacing the already installed 2-2X10.

My approach is to add an Microlam on one side or both sides of the beam. I know the conservative approach is to assume the Microlam will carry all the entire load. This would be the easy way out. However, being an engineer, I want a logical way that I can use with the assumption that both beams are sharing the load proportionally based on their stiffness. So, I can apply prorated load to each one.

My question is, how to come up with a logical prorating percentage?

Please no comment to chastise the contactor nor the owner.
 

Attachments

  • 2-2X10 and LVL Concept-Flattened.pdf
    20.4 KB · Views: 13
Replies continue below

Recommended for you

1735058388141.png
I know the conservative approach is to assume the Microlam will carry all the entire load. This would be the easy way out.
This is probably what I would do. There's nothing wrong with taking the easy way out IMO. I know this isn't really your question, but to elaborate, I would consider using LVLs along both sides and a through bolted connection. This would result in a nice symmetric section that's well connected.

Anyway, on to your actual question:
I want a logical way that I can use with the assumption that both beams are sharing the load proportionally based on their stiffness.
I feel like you just answered your own question. Why not calculate the stiffness, EI, for the 2-2x10, then the LVL, and use those values to determine how the load would be shared?

Along the same lines, you could scale the width of the LVL proportionate to the moduli of elasticity: E_LVL / E_SYP. So, if E_LVL is 2,800,000 psi and E_SYP is 1,400,000 psi, for example, you could say that the 1.75" wide LVL has equivalent stiffness to a 3.5" wide SYP beam (1.75 * 2,800,000 / 1,400,000). Based on these rough numbers, and assuming there's a load path from the applied load to the new LVL piece, you could conclude that the 1.75" LVL (3.5" SYP equivalent) is a little bit stiffer than the 3" wide SYP beam.

Hopefully that helps.
 
View attachment 2724

This is probably what I would do. There's nothing wrong with taking the easy way out IMO. I know this isn't really your question, but to elaborate, I would consider using LVLs along both sides and a through bolted connection. This would result in a nice symmetric section that's well connected.

Anyway, on to your actual question:

I feel like you just answered your own question. Why not calculate the stiffness, EI, for the 2-2x10, then the LVL, and use those values to determine how the load would be shared?

Along the same lines, you could scale the width of the LVL proportionate to the moduli of elasticity: E_LVL / E_SYP. So, if E_LVL is 2,800,000 psi and E_SYP is 1,400,000 psi, for example, you could say that the 1.75" wide LVL has equivalent stiffness to a 3.5" wide SYP beam (1.75 * 2,800,000 / 1,400,000). Based on these rough numbers, and assuming there's a load path from the applied load to the new LVL piece, you could conclude that the 1.75" LVL (3.5" SYP equivalent) is a little bit stiffer than the 3" wide SYP beam.

Hopefully that helps.
Thanks for the response. Your thinking and approach lines up 100% with mine.

Cheers!
 
The added LVL is not going to pick up the existing dead load, unless you somehow unload the existing beam. So the load sharing will only be for the live load.
 
The added LVL is not going to pick up the existing dead load, unless you somehow unload the existing beam.
That's a good point. You could also jack up the existing beam before sistering the new LVL if this is a concern.
 
The added LVL is not going to pick up the existing dead load, unless you somehow unload the existing beam. So the load sharing will only be for the live load.
You are correct. The plan to consider loading the LVL for the live and wind loads only. It s to risky, I think, to jack the beam and alleviate the dead load.
 
Sounds unnecessarily convoluted. It's almost some kind of bridge sequencing calc. It also looks like the trusses are being used "implicitly" to brace the beam. That could use some attention. And since there's a roof involved may as well mention uplift where the beam isn't going to be meaningfully braced on the bottom.

At any rate, to contribute in a more positive fashion, the preload (dead load) won't transfer out unless you shore it first, if you don't, the connections have to be scaled for the load that your stiffness analysis says the LVL "wants" to take, or you design a sufficient transfer that's less than this with your connections to produce a safe condition for a lesser load.

I would not try to connect them for composite action via shear flow or something, just vertical load. Or to stabilize the LVL against the (2) 2x12s for bending.

There's also potentially the argument that the truss is going to force load transfer without a specific connection as the (2) 2x12 will deflect downward when (over) loaded and force bearing on the LVLs, provided the truss doesn't crush. Bearing enhancer?

Deflection will be a bit fuzzy, but if they enclose it late in the process it may not crack down the road.
 
My thoughts about this:
a) I like simple and approximate solutions rather than exact solutions. I'm not doing a PhD thesis for every small project. Not worth my time, not worth the client's money.

b) Simple Option #1, just share the total load between the two beams based on their relative stiffnesses. Simple, but not 100% accurate based on the fact that there is already load in the existing beam. Slight modification where you just share any new load between the beams. Maybe event split dead load into existing and future (super-imposed).

c) Simple Option #2: You could calculate the total capacity of the two beams and assume that any existing load will get "shared" as the beams approach failure.... A friend of mine (who is the best engineer I know) made me do this on a project I worked on for him because Option #1 was putting SLIGHTLY too much load in the new LVL. I don't think this is "technically" correct. KootK was actually the one who pointed this out to me. Tension failure in a wood beam is not all that ductile and load is probably not as shared like this near failure. That being said, I don't think this method is really all that dangerous either. As long as the method #1 is close to working.

My point being that if it calcs out on paper using a method you know isn't 100% correct, that's okay..... As long as your engineering judgment tells you that you're comfortable with the design.
 
Great points above. I've often used an approach similar to "Simple Option #2." If each beam, analyzed independently, were to "fail" by a factor less than 2, I don't think I'd lose any sleep over that solution, at least not for a conventionally framed wood floor. I can't imagine one beam failing independent of the other.
 