I have a question that was asked by a contractor that made me a little sick to my stomach.
The contractor is involved with a job where the steel erector installed the wrong size shear studs. The slab construction was a 4-1/2” slab on 2” composite deck with a required shear stud length of 3-1/2” (the minimum for 2" deck according to the AISC). The erector decided to weld shear studs that were less than 3-1/2”. The mistake was never picked up until after the slab was poured.
Everyone is now learning the AISC requirements of extending the stud 1-1/2” above the height of the deck very quickly. However, they are trying to figure out how to fix the problem. I suggested one of 4 possibilities all of which are undesirable.
1) Rip out the slab and place new shears studs and re-pour slab.
2) Drill holes in the slab (evenly spaced) weld on new proper sized studs and set in non-shrink grout.
3) Install new beam in-between existing to support the floor and place new column under the girders (this is above a basement).
4) Reinforce the existing beams to support the floor w/o composite action.
Is there any other options I would be missing?
The contractor is involved with a job where the steel erector installed the wrong size shear studs. The slab construction was a 4-1/2” slab on 2” composite deck with a required shear stud length of 3-1/2” (the minimum for 2" deck according to the AISC). The erector decided to weld shear studs that were less than 3-1/2”. The mistake was never picked up until after the slab was poured.
Everyone is now learning the AISC requirements of extending the stud 1-1/2” above the height of the deck very quickly. However, they are trying to figure out how to fix the problem. I suggested one of 4 possibilities all of which are undesirable.
1) Rip out the slab and place new shears studs and re-pour slab.
2) Drill holes in the slab (evenly spaced) weld on new proper sized studs and set in non-shrink grout.
3) Install new beam in-between existing to support the floor and place new column under the girders (this is above a basement).
4) Reinforce the existing beams to support the floor w/o composite action.
Is there any other options I would be missing?