what is the possible cause if the suction pressure of my compressor is low and the discharge is very. thank you
 
Replies continue below

Recommended for you

You have double posted ,
Look at the quantity of refrigerant in the system, you appear to be low.
B.E.


You are judged not by what you know, but by what you can do.
 
thanks for the information. its already deleted sir.
sir may i know that is the maximum suction and discharge pressure using r22. thank you very much
 
In my opinion, if both suction and discharge pressure is low, it would be refrigerant charging low.But, if suction side is low and discharge is very high, it may block something in condenser tube and exp valve.
 
Low suction pressure can also indicate poor airflow over the evaporator coil. Get a 608 qualified technician to put a set of gauges onto your system to verify superheat, as well as verifying airflow and fan speeds on the system.
B.E.

You are judged not by what you know, but by what you can do.
 