Concrete Edge Breakout Failure!
tristan861
77
I'm struggling with a steel tube to R.C slab shear connection. I have a 600 kN (Vu) in vertical direction which causes huge failure regarding concrete breakout vertically.
Rods are chemical -post installed- rods (Embedment Length = 300 mm).
Ca1 = 100 mm ( distance from center of last rod to concrete edge).
The slab is already placed.
based on Eq (D-31),ACI 318-11. I have Vcbg = 36 kN only which leads to design ratio of 1660% !! Any idea how to change the concept of connecting to solve this issue?
Please see sketch attached.
Thank you,
 https://files.engineering.com/getfile.aspx?folder=f7153667-0ee4-4a81-886e-2c71e287dfce&file=20180724_162929.jpg
Thats a large load to bring into a slab edge with little edge distance. You need something deeper than the slab, or to add a steel member somehow to grab the tube, and the steel can attach to a concrete element with more 'meat' to it.
If my math is right, thats 134K? Can you do some bent dowels off the back of your plate and have them take that load in tension and develop into the beam?
I think there is alot more to check, but thats my first thought. How are you handling the bending in the beam?
If your slab can handle it, it could. you would need that top plate to be quite stiff. You might be better off just using a bearing type connection if it can figure as the anchors into the slab edge will always struggle to have enough capacity.
I'm not familiar with the equation you're using, so forgive my ignorant question. Is the capacity you're calculating based on the edge distance for the 2 bolts nearest the edge, or is the greater edge distance of the other bolts accounted for?
If you've accounted for the capacity of the bolt group as a whole, you may not have any choice but to change the configuration of the connection. The most effective way I can see would be to extend a plate over the top of the slab (or remove of a portion of the top of the slab to embed a plate or T section) so that it becomes a bearing load on the slab, rather than a shear load on the edge. If that's not an option, extending the connection out along the slab may be the only way.
