RFreund
Structural
- Aug 14, 2010
- 1,885
My main question here is in regards to the water / cement ratio and if you apply a limit on this. However, any input on what you typically check for in regards to a typical concrete mix design review would be helpful.
Below are some typical checks and my question regarding W/C ratios.
For footings/foundation walls:
Concrete strength (typically historical data)
Maximum aggregate size
Air Entrainment
W/C ratio - for foundation walls and footings, this would be Exposure category S per ACI 318. However I'm unsure how to judge which severity applies? If it falls in S0 then there is no limit on W/C. Do you have a limit that you typically apply to this?
For Interior Slabs:
Concrete strength (typically historical data)
Maximum aggregate size
Air Entrainment (typically none or small)
W/C ratio - Here the severity would be F0 (at least for most cases) so again there is no limit on W/C. Do you have a limit that you typically apply to this?
For Exterior Slabs:
Concrete strength (typically historical data)
Maximum aggregate size
Air Entrainment (typically none or small)
Maximum aggregate size
Air Entrainment
W/C ratio - for foundation walls and footings, this would be Exposure category F per ACI 318. Typically where I am at there severity would be F1-F3. However I'm unsure how to judge which severity applies? If it falls in S0 then there is no limit on W/C. Do you have a limit that you typically apply to this?
In a particular case I am looking at a 0.63 W/C with 4" of sump (didn't realize that was possible) for an interior slab. This seems high but the historical cases meet strength requirements. The slab use is office space. Any thoughts on this?
Thanks!!
EIT
Below are some typical checks and my question regarding W/C ratios.
For footings/foundation walls:
Concrete strength (typically historical data)
Maximum aggregate size
Air Entrainment
W/C ratio - for foundation walls and footings, this would be Exposure category S per ACI 318. However I'm unsure how to judge which severity applies? If it falls in S0 then there is no limit on W/C. Do you have a limit that you typically apply to this?
For Interior Slabs:
Concrete strength (typically historical data)
Maximum aggregate size
Air Entrainment (typically none or small)
W/C ratio - Here the severity would be F0 (at least for most cases) so again there is no limit on W/C. Do you have a limit that you typically apply to this?
For Exterior Slabs:
Concrete strength (typically historical data)
Maximum aggregate size
Air Entrainment (typically none or small)
Maximum aggregate size
Air Entrainment
W/C ratio - for foundation walls and footings, this would be Exposure category F per ACI 318. Typically where I am at there severity would be F1-F3. However I'm unsure how to judge which severity applies? If it falls in S0 then there is no limit on W/C. Do you have a limit that you typically apply to this?
In a particular case I am looking at a 0.63 W/C with 4" of sump (didn't realize that was possible) for an interior slab. This seems high but the historical cases meet strength requirements. The slab use is office space. Any thoughts on this?
Thanks!!
EIT