Samwise Gamgee
Structural
- Oct 7, 2021
- 113
The GC has sent an RFI about the concrete test samples . The concrete supplier mentioned industry standards suggests sampling the concrete before pumping it out of the truck.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Commentary on CSA said:Unless otherwise written in the contract
specifications or agreed upon at the pre-construction
or pre-placement meetings, sampling for the
purposes of acceptance shall be a grab sample
obtained between 10% and 90% of the load at the
point of discharge. This requirement is not applicable
if the concrete is to be tested for slump prior to the
addition of superplasticizer.
CSA A23.1 said:A23.1-14 – Clause 4.4.2 Sampling concrete
Samples of concrete for testing purposes shall be
secured in accordance with CSAA23.2-1C. When the
owner elects to assess the quality of concrete at a
location other than the point of discharge from the
delivery equipment, the owner shall state the point from
which the samples shall be taken.
Note: The point at which the concrete is sampled will
depend on the intended use of the test information.
Where the test data are intended to give information on
the properties of the concrete
(a)as delivered to the site, the concrete should be
sampled at the point of discharge from the delivery
equipment; or
(b) as incorporated into the structure, the concrete
should be sampled as close to the point of final deposit
in the form as is practicable.